[OPLINTECH] Building question: isolated ground or at least separate circuits, and built-in surge protection

Chad Neeper cneeper at level9networks.com
Tue Jul 21 10:15:33 EDT 2009


Just to expound a bit:

The bundling of cables Bob is talking about is because of inductance. If 
one wire is energized (even during normal use), the energy can induce 
the electrons in a nearby parallel wire to become active, causing the 
power surge to "hop" wires, even if they aren't physically connected to 
each other. This is the reason for keeping higher risk lines at least 12 
inches from lower risk lines and for crossing each other 
perpendicularly. In normal use, this feature can cause electrical 
"noise" on nearby wires, reducing signal quality. Normally, this isn't 
much of a problem in, for instance, bundled low voltage ethernet cables 
at the rack. However, in a power surge situation, bundled wires can be a 
way for non-connected wires to further the damage.


-----------------------
Chad Neeper
Senior Systems Engineer

Level 9 Networks
740-548-8070 (voice)
866-214-6607 (fax)

--   Full LAN/WAN consulting services   --
-- Specialized in libraries and schools --



Bob Neeper wrote:
> Since Chad mentioned my name...Here 's a few thoughts. Some duplicates 
> of Chad's.
>
> We did have a few hits and lost a couple of PC's, telephone module, etc
> Also some electronics in the main power distribution panel when a bird 
> fried on the pole.
>
> Point of interest.
> A static spark from your finger to a doorknob can be over 6,000volts.
> It can easily destroy or damage an electronic chip, depending on contact.
> Lightning can be over 300 kilovolts for a few milliseconds.
>
> With a direct hit it probably won't matter too much what you have.
> Mettler-Toledo sold many truck scale protection kits in lightning 
> prone areas and still lost load cells.
> (Load cells generate low voltage signals representing weight changes.)
>
> Always keep your insurance paid up !
> Make certain the coverage is correct !
> Keep your inventory list up to date and handy!
>
> M-T headquarters has a nice setup for their workstations.
> Each one has it's own special surge protected.power distribution box.
> Some outlets were for printers etc. Ethernet and phone lines too if I 
> remember correctly.
> Special outlets for the PC and monitor went straight to a battery 
> backup system.
> It had a BIG battery bank and an outside emergency generator.
>
> Fiber optic cables are very nice, they won't conduct surges.
> Just having an Ethernet cable close to power cables could knock out a NIC.
> As Ethernet cables are usually bundled from the rack you could easily 
> take out every attached NIC.
> Racks can come with built in surge protection,   for a few dollars more.
> APC ProtectNet can be used at the PC
>
> M-T always specified low voltage cables to be at least a foot away 
> from AC cables.
> Never directly next to a power cable and only cross at right angles.
>
> So don't tie wrap Ethernet cables with the AC power cords because it 
> makes a neat bundle.
> Keep the mouse, k/b, and monitor signal cable separate too.
> Definitely don't tie anything to the surge protector power cable!
>
> Have the power company insure there is lightning protection at the 
> pole transformer.
> Add something similar to the main power distribution panel in the 
> building.
>
> Don't forget to protect the T1  (or whatever) cable and the alarm 
> system phone line.
> Maybe even consider 2 inline protectors.
> An alarm installer saved his unit this way. The first one blew off the 
> wall.
> The second died to save his system.
>
> Especially protect power and Ethernet outlets on outside walls.
> We lost a  NIC and the a single port on the switch at the other end.
> And the hit was waaaayy  over there somewhere.
>
> Bob
>
>
> R. W. (Bob) Neeper     Cell: (740)-407-3572 
> Community Library
> 44 Burrer Dr.
> Sunbury, Oh 43074
> Tel:  (740)-965-3901
>
>
> Chad Neeper wrote:
>> Excellent questions! With the exception of the server room and/or 
>> wiring closets:
>>
>> Speaking from my own experience and observations, I'd suggest not 
>> paying particular attention to having isolated grounds or even 
>> necessarily isolated circuits for your general use patron and staff 
>> computers. Naturally, however, DO pay attention to the estimated load 
>> on each circuit. If it's intended to have a large number of 
>> workstation at a particular location (a lab, for instance), then of 
>> course you'll need to figure out how many computers you can have on 
>> one circuit and then have enough circuits run to keep your load WELL 
>> below the maximum loads. Same goes for anywhere that you know you are 
>> going to have devices (computer or otherwise) that draw power. This 
>> is an interesting read I stumbled upon with a quick Google search 
>> about IG systems and how they might NOT work as you might think. I 
>> suppose this could affect its use in a server room as well and worth 
>> investigating further, probably best with a full-blooded 
>> electrical/electronics engineer:
>>
>> http://ecmweb.com/mag/electric_demystifying_isolated_grounded/index.html
>>
>> Definitely food for thought, especially when you factor in the added 
>> costs of an IG system.
>>
>> As for whole-building surge suppression, it would seem that a 
>> whole-building surge suppressor is a good way to go, but it would be 
>> wise not to rely on it completely. You should still use point-of-use 
>> surge suppressors to protect your more valuable items...computers, 
>> electronics, all the normal stuff, etc. You'll have to work with your 
>> general/electrical contractor to work out if you want circuit-based 
>> suppression or whole-building and to find out what options are 
>> available to you. While I don't know what commercial-grade 
>> whole-building surge suppressors are available, I suspect that you 
>> just might find the cost to be perfectly acceptable as a one-time 
>> cost insurance policy. (If lightning were to strike within 1/2 mile 
>> from the library, how many devices are plugged in 24/7 that might get 
>> fried or degraded. When the power goes out, or more specifically, 
>> when it comes back on again and "yo-yos" as it often will...how many 
>> devices are having their lifespans degraded and what is the cost to 
>> replace/repair those items? Think refrigerator, furnace control 
>> system, dishwasher, alarm system...anything electronic...) As for how 
>> common it is...Well, amongst my own library clients, not a single one 
>> currently has a whole-building or whole-circuit surge suppression. I 
>> can quickly name several clients that might have benefited from it, 
>> however!
>>
>> Also consider the fact that your phone system is expensive/important 
>> and that power surges can travel just as readily into your library 
>> via a telephone line. If you protect the lines at the point they 
>> enter your building you just might save yourself a major expense and 
>> headache down the road. Again...I have several libraries that pop to 
>> mind here too...and, at the time, those each had only 3-4 analog 
>> phone lines that could easily have been protected with off-the-shelf 
>> protection just before they entered the multi-thousand dollar phone 
>> systems...for under $150 total. Those were hard-earned lessons! 
>> Actually, I think Bob Neeper might have been around for one of these 
>> incidents. He can attest to this one!
>>
>> Same with network data cables...You can get surge suppressed 
>> rack-mount data ports to replace your "normal" rack-mount ports. But 
>> last time I looked, they weren't particularly cheap. Unless you have 
>> a smallish number of computers, you might be limited to protecting 
>> select computers. Seven or eight years ago Hurt/Battelle Memorial 
>> Library was hit with a direct lightning strike. At the time they had 
>> about 26 six(ish)-month old computers. All but four or five had 
>> immediate damage to the network cards, with the mainboards failing 
>> completely shortly after. Having dutifully protected every computer 
>> with good surge suppressors, none of the power supplies failed during 
>> the period the computers remained in sporadic use. Thank goodness for 
>> good insurance!!!
>>
>> Good luck!
>> Chad
>>
>>
>> -----------------------
>> Chad Neeper
>> Senior Systems Engineer
>>
>> Level 9 Networks
>> 740-548-8070 (voice)
>> 866-214-6607 (fax)
>>
>> --   Full LAN/WAN consulting services   --
>> -- Specialized in libraries and schools --
>>
>>
>>
>> Phil Shirley wrote:
>>> Could you help me with these two questions about electrical systems for
>>> computer equipment?  We're planning a renovation of the main part of 
>>> our
>>> library.
>>>
>>> 1.  Should we have electrical circuits with an isolated ground, or at
>>> least separate electrical circuits, for our computer equipment?  
>>> (I'm talking about workstations around the library, as well as 
>>> everything in our server room.)  I assume the answer is yes, but 
>>> early drafts of the electrical plans do not have anything like 
>>> this.  One of the EEs told me that often, instead of having a true 
>>> isolated ground setup, many places will simply have separate 
>>> circuits designated for computer equipment (with orange outlets); 
>>> supposedly, the ground noise that's caused by a sweeper or something 
>>> doesn't travel far enough to be of concern to a computer on a 
>>> separate circuit.  A little bit of searching suggests that maybe a 
>>> true isolated ground system is not necessary for most modern 
>>> computer equipment.
>>>
>>> 2.  Is it common to have surge protection built into the electrical 
>>> system, as opposed to plugging surge protectors into the wall and 
>>> plugging computers into those?  I'm told that it's possible to have 
>>> surge protection built into the electrical system in any of several 
>>> places, but I don't know if it's cost-efficient for most organizations.
>>>
>>> Phil
>>>   
>> ------------------------------------------------------------------------
>>
>> _______________________________________________
>> OPLINTECH mailing list
>> OPLINTECH at oplin.org
>> http://mail.oplin.org/mailman/listinfo/oplintech
>> Search: http://oplin.org/techsearch
>>   
> ------------------------------------------------------------------------
>
> _______________________________________________
> OPLINTECH mailing list
> OPLINTECH at oplin.org
> http://mail.oplin.org/mailman/listinfo/oplintech
> Search: http://oplin.org/techsearch
>   
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://mail.oplin.org/pipermail/oplintech/attachments/20090721/65b81db9/attachment-0001.html
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smime.p7s
Type: application/x-pkcs7-signature
Size: 3273 bytes
Desc: S/MIME Cryptographic Signature
Url : http://mail.oplin.org/pipermail/oplintech/attachments/20090721/65b81db9/smime-0001.bin


More information about the OPLINTECH mailing list