<div dir="ltr"><div>Is it that the UPS electronics are actually becoming damaged or is the problem really the frequency with which you're needing to replace the batteries? With such poor power, you're probably cycling the batteries often, which will greatly reduce the lifespan of the batteries. There are a few things you might be able to do to decrease the wear on the batteries. For starters, you might be able to decrease the sensitivity of the UPS so that it doesn't switch to battery quite as often. In the following short White Paper, refer to the sections on Ambient Temperature and Cycling to help maximize your battery life.<br></div><div><div><br></div><div><a href="http://www.apcmedia.com/salestools/VAVR-9MNSWC/VAVR-9MNSWC_R0_EN.pdf" target="_blank">http://www.apcmedia.com/salestools/VAVR-9MNSWC/VAVR-9MNSWC_R0_EN.pdf</a><br></div><div><br></div><div><div>If it's so bad that you're destroying your equipment cabinet UPS's electronics, I'd think you'd have cause to involve the power company. And if it's so bad that you're destroying the electronics rather than just degrading the batteries, are you not also having problems for all other electronic equipment in the building? If not, then maybe why not?</div></div><div><br></div><div>If your UPS electronics are failing, then you're probably also losing/degrading computers and other electronic equipment elsewhere in the building. That sounds like maybe a whole-building solution might actually be warranted. Or definitely an attempt to get the power company to clean up their act, if you haven't already! If you're NOT having problems elsewhere, then is there something with/on/near that circuit that's contributing to the problem?</div></div><div><br></div><div>Anyway, if you're currently using a stand-by UPS, you might consider looking into a line interactive UPS instead, which may do a better job. If you're using a 1500VA UPS, there's probably a pretty good chance that it's already a line interactive UPS, but worth double-checking the manufacturer's specs. Here's another white paper about the various types of UPSes:</div><div><br></div><div><a href="http://www.apcmedia.com/salestools/SADE-5TNM3Y/SADE-5TNM3Y_R7_EN.pdf" target="_blank">http://www.apcmedia.com/salestools/SADE-5TNM3Y/SADE-5TNM3Y_R7_EN.pdf</a><br></div><div><br></div><div><br></div><div>If you're already using a line interactive UPS, maybe you need to bump up to a double-conversion on-line UPS. It's more technical than the previous one, but it's worth reading the comparison between the two technologies you can choose from in the 750 to 5000VA range:</div><div><br></div><div><a href="http://www.apcmedia.com/salestools/JSII-5YQSBR/JSII-5YQSBR_R1_EN.pdf">http://www.apcmedia.com/salestools/JSII-5YQSBR/JSII-5YQSBR_R1_EN.pdf</a><br></div><div><br></div><div>Can you tell I prefer Schneider Electric (APC) for power conditioning?  :-)<br></div><div><br></div><div><br></div><div><br></div><div><div>My final suggestion would be to visit your favorite UPS manufacturer's website and find a list of their Ohio partners to see if you can contact a professional installer that is willing to talk to you about the best specific UPS model for your environment.</div></div><div><br></div><div><br></div><div>HTH and good luck!</div><div>Chad</div></div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr"><div>______________________________<br><b>Chad Neeper</b><br><font size="1">Senior Systems Engineer</font><br><br><b>Level 9 Networks</b><br><font size="1">740-548-8070 (voice)<br>866-214-6607 (fax)</font><br><br><font size="1"><i>Full IT/Computer consulting services -- Specialized in libraries and schools</i></font><br></div></div></div></div>
<br><div class="gmail_quote">On Wed, Aug 5, 2015 at 2:47 PM, Becky Schultz <span dir="ltr"><<a href="mailto:b.schultz@yourppl.org" target="_blank">b.schultz@yourppl.org</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Hi!<br>
<br>
We have a branch that, due to extremely dirty power coming into the building, we keep having to replace the UPS in the network cabinet. Our electrician has also confirmed this is why the units are failing.  A 1500VA UPS is plenty big enough, but we apparently need a unit with more high end power conditioning.  A whole building solution isn't justified, so I'm just looking for feedback or suggestions on equipment to protect our relatively small rack of equipment.<br>
<br>
Thanks!<span class="HOEnZb"><font color="#888888"><br>
<br>
-- <br>
Becky Schultz<br>
Technology Coordinator | Portsmouth Public Library<br>
<a href="tel:%28740%29%20354-5688%20ext.10518" value="+17403545688" target="_blank">(740) 354-5688 ext.10518</a> | <a href="mailto:b.schultz@yourppl.org" target="_blank">b.schultz@yourppl.org</a> | <a href="http://www.yourppl.org" rel="noreferrer" target="_blank">http://www.yourppl.org</a><br>
<a href="http://www.twitter.com/portsmouthpl" rel="noreferrer" target="_blank">http://www.twitter.com/portsmouthpl</a> | <a href="http://www.facebook.com/yourppl" rel="noreferrer" target="_blank">http://www.facebook.com/yourppl</a><br>
_______________________________________________<br>
OPLINTECH mailing list<br>
<a href="mailto:OPLINTECH@lists.oplin.org" target="_blank">OPLINTECH@lists.oplin.org</a><br>
<a href="http://lists.oplin.org/mailman/listinfo/oplintech" rel="noreferrer" target="_blank">http://lists.oplin.org/mailman/listinfo/oplintech</a><br>
<br>